Quote:
Originally Posted by tlgerdes
Get at least a 3kva unit and make yourself a 3pin male to male adaptor. That way you can cut the main breaker, then plug the gen into any house socket and power the whole house.
Just remember to disconnect gen before reconnecting the main breaker.
|
Sorry Trevor,
This advice is negligent.
Firstly, nobody should ever have a 3 pin male to male cable laying
around the house.
All it takes is for is for someone to plug it into a live outlet
and they could injure or kill themselves.
Secondly, if the user does not open the main breaker in the fuse box
or if the main breaker is faulty, you will put 240V back up the line.
If there is a linesmen working on the line elsewhere and they have
assumed the line is safe to effect a repair, you could kill them.
I recommend to edit the post to redact the advice in question.
Best regards
Gary Kopff
Member IEEE