My original training was in irrigation design and then valve sales.

Valve operating normally when operated manually -

Still blowing fuse, new solenoid -

Valve blockage (though none exists) has no relation to blowing fuse - these solenoids are designed to be active duty cycle for loooong extended periods.

Problem is probably further up the control line - eg transformer 240VAC to 24VDC is short circuiting.